The plans state that I use 38 x 50 f8 for roof battens(600cntr) finding the stuff hard to get does anyone see the problem of using MGp10 90x45 ?
barney118
5th Mar 2012, 07:17 PM
More info needed,roof type truss etc and color bond vs tile and distance of rafter
mullfitz
5th Mar 2012, 08:48 PM
More info needed,roof type truss etc and color bond vs tile and distance of rafter
Colorbond Roof LVL rafters 190x43 spacing of 900 Span of 5 m skillon roof
Hope that helps
Moondog55
5th Mar 2012, 09:48 PM
Can you rip? Cut the 90 * 45 down the guts and use half each 45*45.
I think they are functional equivalents
ringtail
5th Mar 2012, 09:50 PM
I use Hyne T3 90 x 45 mgp 12 when spanning 900 but 70 x 45 mgp 12 would do the job also from memory
mullfitz
5th Mar 2012, 10:58 PM
Can you rip? Cut the 90 * 45 down the guts and use half each 45*45.
I think they are functional equivalents
What about F8 35 x 25 hardwood
ringtail
6th Mar 2012, 12:12 AM
Not meaty enough
barney118
6th Mar 2012, 06:54 AM
i used 90 x 45 MGP12 which is easy to get and spans 900 as ringtail says. The existing house was screwed to HW battens and its a right PITA. F8 is not a hardwood recheck your desdign and correct span tables, is a grading system usually for treated pine outdoor use. Use T2 which is used for indoor covered applications for termite protection.
barney118
6th Mar 2012, 08:44 AM
Mgp10 90x45 is good to span1200 on sheet roof at 1200 spacing
barney118
6th Mar 2012, 11:29 AM
I stand corrected there is span tables for the f8 unseasoned. Since when is f8 a hardwood?
A tip for screwing your battens down offset the screws to your rafters so when you screw your sheets down the screw will line up with the centre of the batten and you won't hit your screws.you may even nail to rafters I just went for overkill
mullfitz
6th Mar 2012, 10:20 PM
What about mgp10 7o x 35
ausdesign
7th Mar 2012, 10:01 AM
45*70 mgp10 or 35*70 mgp12
intertd6
7th Mar 2012, 09:11 PM
I don't know what state your in but most hwds in nsw will go F14 & is used commonly for battens, 50 X 38 is also a common size & readily available.
regards inter
barney118
7th Mar 2012, 09:20 PM
70x35 mgp10 only good for 650 span
mullfitz
7th Mar 2012, 10:52 PM
I don't know what state your in but most hwds in nsw will go F14 & is used commonly for battens, 50 X 38 is also a common size & readily available.
regards inter
The plans state 50 x 38 f8 (600 spacing)hardwood but finding that hard to get does that seem right ?
ringtail
7th Mar 2012, 11:02 PM
You could always use metal top hat like on most new houses. Cheap, light and ultra strong
barney118
8th Mar 2012, 01:35 AM
Think about what you are after here, span means distance between rafter/truss, spacing means number of batten rows needed. The further between spacings reduce total linear metres of material and less labour costs. I find it better to use wood battens on a house as when laying insulation blanket you can get it tight using foil clips.
mullfitz
8th Mar 2012, 08:24 AM
You could always use metal top hat like on most new houses. Cheap, light and ultra strong
Thanks for that am I still looking at 600 spacing or can go to 900 withe top hat
Moondog55
8th Mar 2012, 01:08 PM
Funny; I have just finished talking with my builder cousin, he says that a 90*45 MGP12 is fine if cut in half and used as a 45*45 as it is the thickness of the timber that counts most
ausdesign
8th Mar 2012, 02:25 PM
45*45 doesn't meet the timber framing code
ringtail
8th Mar 2012, 03:47 PM
900 with a 65 mm top hat no problem. You will see pro roofers running a batten between the 900's (at 450 ctrs) but it is quite small insection and there only to support the roof blanket and make it harder for them ( roofers) to fall between the trusses as they are working.
barney118
8th Mar 2012, 05:28 PM
45*45 doesn't meet the timber framing code
:whs:
mullfitz
8th Mar 2012, 08:21 PM
What about 40mm will that give me 900
shauck
9th Mar 2012, 08:15 AM
2010 span tables - MGP10 90x45 - spacing at 600 or 900 will both span 1200
- F8 USHW 38x75 - spacing 600 will span 1150 or spacing 900 will span 900
ausdesign
9th Mar 2012, 10:42 AM
The batten spacing for corrugated iron roofing is a maximum of 1200 on internal runs & 900 spacing at the sheet ends.(0.47 custom orb)
I assume that the colorbond mentioned in your first post refers to corrugated iron. If it is a 'tray deck' then there are differing max. spacings depending upon the product used.
Pine battens are used by many builders as it is generally easier to source than unseasoned hardwood (OB) & is easier to work with as far as straightening & it comes as H2 for termite protection.
A timber product is also easier to fix down RFL which is now standard under steel roofing.
'Top hat' sections are used frequently by steel frame manufacturers as it fits with their system & their 'buying power'.
With a rafter spacing of 900 I would generally nominate 35*70 MGP12 battens at 900 centres.
The calculation in the timber framing code also takes into account the 'uplift' capacity strength of the member. Having said that at an N2 design wind gust speed 35*70 mgp12 will span 1050 & at C4, cyclone rating will span 1000.
As an aside - 35*70 is different to 70*35 etc etc. The first figure relates to height.
barney118
9th Mar 2012, 01:48 PM
Peter where does .47 c/orb as a sheet stated? As the standard for domestic is 0.42mm, 0.47 is used more in a commercial side.
ausdesign
9th Mar 2012, 02:13 PM
My understanding is that 0.42 is the BMT. 0.47 is the TCT
ausdesign
9th Mar 2012, 02:54 PM
My understanding is that 0.42 is the BMT. 0.47 is the TCT
Base metal thickness & total coated thickness
mullfitz
9th Mar 2012, 10:23 PM
Thanks for the help
I am using 190 x 45 LVL for the rafters and 40 mm top hats at 600mm spacing
mullfitz
11th Mar 2012, 09:48 AM
Thanks for the help
I am using 190 x 45 LVL for the rafters and 40 mm top hats at 600mm spacing
Also does the foil insulation go on before or after the battens
ausdesign
13th Mar 2012, 11:52 AM
Before
barney118
13th Mar 2012, 12:36 PM
I have always put insulation on after battens, otherwise how do you support between rafters. The pros use magnets for top hats I believe to keep tight. For me I used foil clips to wood battens which is easier.
ausdesign
13th Mar 2012, 01:03 PM
If we're talking RFL, then it's better to lay it over the rafters, creating a batten air space to the underside of the roofing iron. With the RFL layed parallel to the guttering & overlapped it acts as a sarking as well.
In a 'blanket' situation (rfl + batt) it is possibly easier to lay the product down the slope of the roof, dished over the battens, but with this application there is always the probability of moisture (condensation) penetrating into the roof space through the overlaps.