    The plans state that I use 38 x 50 f8 for roof battens(600cntr) finding the stuff hard to get does anyone see the problem of using MGp10 90x45 ?

  2. #2
    barney118's Avatar
    barney118 is offline 1K Club Member
    Join Date
    Jan 2008
    Location
    NSW
    Age
    42
    Posts
    1,689

    Default

    More info needed,roof type truss etc and color bond vs tile and distance of rafter
    cheers Look out if I have a tape measure in my hand.....I'm upto something

  3. #3
    mullfitz is offline Senior Member
    Join Date
    May 2006
    Location
    Australia
    Posts
    124

    Default

    Quote Originally Posted by barney118 View Post
    More info needed,roof type truss etc and color bond vs tile and distance of rafter
    Colorbond Roof LVL rafters 190x43 spacing of 900 Span of 5 m skillon roof

    Hope that helps

  4. #4
    Moondog55 is offline 2K Club Member
    Join Date
    Nov 2009
    Location
    Geelong
    Posts
    2,009

    Default

    Can you rip? Cut the 90 * 45 down the guts and use half each 45*45.
    I think they are functional equivalents

  5. #5
    ringtail is offline 3K Club Member
    Join Date
    Sep 2009
    Location
    brisbane
    Posts
    3,047

    Default

    I use Hyne T3 90 x 45 mgp 12 when spanning 900 but 70 x 45 mgp 12 would do the job also from memory

  6. #6
    mullfitz is offline Senior Member
    Join Date
    May 2006
    Location
    Australia
    Posts
    124

    Default

    Quote Originally Posted by Moondog55 View Post
    Can you rip? Cut the 90 * 45 down the guts and use half each 45*45.
    I think they are functional equivalents

    What about F8 35 x 25 hardwood

  7. #7
    ringtail is offline 3K Club Member
    Join Date
    Sep 2009
    Location
    brisbane
    Posts
    3,047

    Default

    Not meaty enough

  8. #8
    barney118's Avatar
    barney118 is offline 1K Club Member
    Join Date
    Jan 2008
    Location
    NSW
    Age
    42
    Posts
    1,689

    Default

    i used 90 x 45 MGP12 which is easy to get and spans 900 as ringtail says. The existing house was screwed to HW battens and its a right PITA. F8 is not a hardwood recheck your desdign and correct span tables, is a grading system usually for treated pine outdoor use. Use T2 which is used for indoor covered applications for termite protection.

  9. #9
    barney118's Avatar
    barney118 is offline 1K Club Member
    Join Date
    Jan 2008
    Location
    NSW
    Age
    42
    Posts
    1,689

    Default

    Mgp10 90x45 is good to span1200 on sheet roof at 1200 spacing
    cheers Look out if I have a tape measure in my hand.....I'm upto something

  10. #10
    barney118's Avatar
    barney118 is offline 1K Club Member
    Join Date
    Jan 2008
    Location
    NSW
    Age
    42
    Posts
    1,689

    Default

    I stand corrected there is span tables for the f8 unseasoned. Since when is f8 a hardwood?
    A tip for screwing your battens down offset the screws to your rafters so when you screw your sheets down the screw will line up with the centre of the batten and you won't hit your screws.you may even nail to rafters I just went for overkill
    cheers Look out if I have a tape measure in my hand.....I'm upto something

  11. #11
    mullfitz is offline Senior Member
    Join Date
    May 2006
    Location
    Australia
    Posts
    124

    Default

    What about mgp10 7o x 35

  12. #12
    ausdesign's Avatar
    ausdesign is offline Building Designer
    Join Date
    Sep 2004
    Location
    Strzelecki Ranges Victoria
    Posts
    539

    Default

    45*70 mgp10 or 35*70 mgp12
    Peter Clarkson

    www.ausdesign.com.au

    This information is intended to provide general information only.
    It does not purport to be a comprehensive advice.

  13. #13
    intertd6 is offline 1K Club Member
    Join Date
    Nov 2008
    Location
    nsw
    Posts
    1,079

    Default

    I don't know what state your in but most hwds in nsw will go F14 & is used commonly for battens, 50 X 38 is also a common size & readily available.
    regards inter

  14. #14
    barney118's Avatar
    barney118 is offline 1K Club Member
    Join Date
    Jan 2008
    Location
    NSW
    Age
    42
    Posts
    1,689

    Default

    70x35 mgp10 only good for 650 span
    cheers Look out if I have a tape measure in my hand.....I'm upto something

  15. #15
    mullfitz is offline Senior Member
    Join Date
    May 2006
    Location
    Australia
    Posts
    124

    Default

    Quote Originally Posted by intertd6 View Post
    I don't know what state your in but most hwds in nsw will go F14 & is used commonly for battens, 50 X 38 is also a common size & readily available.
    regards inter

    The plans state 50 x 38 f8 (600 spacing)hardwood but finding that hard to get does that seem right ?

  16. #16
    ringtail is offline 3K Club Member
    Join Date
    Sep 2009
    Location
    brisbane
    Posts
    3,047

    Default

    You could always use metal top hat like on most new houses. Cheap, light and ultra strong

  17. #17
    barney118's Avatar
    barney118 is offline 1K Club Member
    Join Date
    Jan 2008
    Location
    NSW
    Age
    42
    Posts
    1,689

    Default

    Think about what you are after here, span means distance between rafter/truss, spacing means number of batten rows needed. The further between spacings reduce total linear metres of material and less labour costs. I find it better to use wood battens on a house as when laying insulation blanket you can get it tight using foil clips.
    cheers Look out if I have a tape measure in my hand.....I'm upto something

  18. #18
    mullfitz is offline Senior Member
    Join Date
    May 2006
    Location
    Australia
    Posts
    124

    Default

    Quote Originally Posted by ringtail View Post
    You could always use metal top hat like on most new houses. Cheap, light and ultra strong
    Thanks for that am I still looking at 600 spacing or can go to 900 withe top hat

  19. #19
    Moondog55 is offline 2K Club Member
    Join Date
    Nov 2009
    Location
    Geelong
    Posts
    2,009

    Default

    Funny; I have just finished talking with my builder cousin, he says that a 90*45 MGP12 is fine if cut in half and used as a 45*45 as it is the thickness of the timber that counts most

  20. #20
    ausdesign's Avatar
    ausdesign is offline Building Designer
    Join Date
    Sep 2004
    Location
    Strzelecki Ranges Victoria
    Posts
    539

    Default

    45*45 doesn't meet the timber framing code
    Peter Clarkson

    www.ausdesign.com.au

    This information is intended to provide general information only.
    It does not purport to be a comprehensive advice.

  21. #21
    ringtail is offline 3K Club Member
    Join Date
    Sep 2009
    Location
    brisbane
    Posts
    3,047

    Default

    900 with a 65 mm top hat no problem. You will see pro roofers running a batten between the 900's (at 450 ctrs) but it is quite small insection and there only to support the roof blanket and make it harder for them ( roofers) to fall between the trusses as they are working.

  22. #22
    barney118's Avatar
    barney118 is offline 1K Club Member
    Join Date
    Jan 2008
    Location
    NSW
    Age
    42
    Posts
    1,689

    Default

    Quote Originally Posted by ausdesign View Post
    45*45 doesn't meet the timber framing code

  23. #23
    mullfitz is offline Senior Member
    Join Date
    May 2006
    Location
    Australia
    Posts
    124

    Default

    What about 40mm will that give me 900

  24. #24
    shauck is offline 2K Club Member
    Join Date
    Oct 2009
    Location
    Daylesford Australia
    Posts
    2,145

    Default

    2010 span tables - MGP10 90x45 - spacing at 600 or 900 will both span 1200
    - F8 USHW 38x75 - spacing 600 will span 1150 or spacing 900 will span 900

  25. #25
    ausdesign's Avatar
    ausdesign is offline Building Designer
    Join Date
    Sep 2004
    Location
    Strzelecki Ranges Victoria
    Posts
    539

    Default

    The batten spacing for corrugated iron roofing is a maximum of 1200 on internal runs & 900 spacing at the sheet ends.(0.47 custom orb)
    I assume that the colorbond mentioned in your first post refers to corrugated iron. If it is a 'tray deck' then there are differing max. spacings depending upon the product used.
    Pine battens are used by many builders as it is generally easier to source than unseasoned hardwood (OB) & is easier to work with as far as straightening & it comes as H2 for termite protection.
    A timber product is also easier to fix down RFL which is now standard under steel roofing.
    'Top hat' sections are used frequently by steel frame manufacturers as it fits with their system & their 'buying power'.
    With a rafter spacing of 900 I would generally nominate 35*70 MGP12 battens at 900 centres.
    The calculation in the timber framing code also takes into account the 'uplift' capacity strength of the member. Having said that at an N2 design wind gust speed 35*70 mgp12 will span 1050 & at C4, cyclone rating will span 1000.
    As an aside - 35*70 is different to 70*35 etc etc. The first figure relates to height.
    Peter Clarkson

    www.ausdesign.com.au

    This information is intended to provide general information only.
    It does not purport to be a comprehensive advice.

  26. #26
    barney118's Avatar
    barney118 is offline 1K Club Member
    Join Date
    Jan 2008
    Location
    NSW
    Age
    42
    Posts
    1,689

    Default

    Peter where does .47 c/orb as a sheet stated? As the standard for domestic is 0.42mm, 0.47 is used more in a commercial side.

  27. #27
    ausdesign's Avatar
    ausdesign is offline Building Designer
    Join Date
    Sep 2004
    Location
    Strzelecki Ranges Victoria
    Posts
    539

    Default

    My understanding is that 0.42 is the BMT. 0.47 is the TCT
    Peter Clarkson

    www.ausdesign.com.au

    This information is intended to provide general information only.
    It does not purport to be a comprehensive advice.

  28. #28
    ausdesign's Avatar
    ausdesign is offline Building Designer
    Join Date
    Sep 2004
    Location
    Strzelecki Ranges Victoria
    Posts
    539

    Default

    Quote Originally Posted by ausdesign View Post
    My understanding is that 0.42 is the BMT. 0.47 is the TCT
    Base metal thickness & total coated thickness
    Peter Clarkson

    www.ausdesign.com.au

    This information is intended to provide general information only.
    It does not purport to be a comprehensive advice.

  29. #29
    mullfitz is offline Senior Member
    Join Date
    May 2006
    Location
    Australia
    Posts
    124

    Default

    Thanks for the help

    I am using 190 x 45 LVL for the rafters and 40 mm top hats at 600mm spacing

  30. #30
    mullfitz is offline Senior Member
    Join Date
    May 2006
    Location
    Australia
    Posts
    124

    Default

    Thanks for the help

    I am using 190 x 45 LVL for the rafters and 40 mm top hats at 600mm spacing

    Also does the foil insulation go on before or after the battens

  31. #31
    ausdesign's Avatar
    ausdesign is offline Building Designer
    Join Date
    Sep 2004
    Location
    Strzelecki Ranges Victoria
    Posts
    539

    Default

    Before
    Peter Clarkson

    www.ausdesign.com.au

    This information is intended to provide general information only.
    It does not purport to be a comprehensive advice.

  32. #32
    barney118's Avatar
    barney118 is offline 1K Club Member
    Join Date
    Jan 2008
    Location
    NSW
    Age
    42
    Posts
    1,689

    Default

    I have always put insulation on after battens, otherwise how do you support between rafters. The pros use magnets for top hats I believe to keep tight. For me I used foil clips to wood battens which is easier.
    cheers Look out if I have a tape measure in my hand.....I'm upto something

  33. #33
    ausdesign's Avatar
    ausdesign is offline Building Designer
    Join Date
    Sep 2004
    Location
    Strzelecki Ranges Victoria
    Posts
    539

    Default

    If we're talking RFL, then it's better to lay it over the rafters, creating a batten air space to the underside of the roofing iron. With the RFL layed parallel to the guttering & overlapped it acts as a sarking as well.
    In a 'blanket' situation (rfl + batt) it is possibly easier to lay the product down the slope of the roof, dished over the battens, but with this application there is always the probability of moisture (condensation) penetrating into the roof space through the overlaps.
    Peter Clarkson

    www.ausdesign.com.au

    This information is intended to provide general information only.
    It does not purport to be a comprehensive advice.

LinkBacks (?)

  1. 9th Mar 2012, 10:21 PM

Similar Threads

  1. Span of 5 metres using mgp10
    By mullfitz in forum ROOFING
    Replies: 1
    Last Post: 24th Jul 2011, 12:08 AM
  2. Replies: 0
    Last Post: 17th Mar 2011, 10:11 PM
  3. can i use mgp10 for framing
    By oohsam in forum STRUCTURAL RENOVATION
    Replies: 5
    Last Post: 10th Aug 2009, 06:11 PM
  4. Maximum hole size in a 90x45 wall stud
    By hayaku in forum STRUCTURAL RENOVATION
    Replies: 5
    Last Post: 23rd Jul 2009, 07:59 AM
  5. small deck with 90x45 bearers
    By dub3media in forum DECKING
    Replies: 1
    Last Post: 21st Mar 2008, 06:43 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •