Brivis Buffalo 85 EMS OH/F & OH/S errors

Results 1 to 2 of 2
  1. #1
    Member
    Join Date
    May 2012
    Location
    Melbourne
    Posts
    52

    Default Brivis Buffalo 85 EMS OH/F & OH/S errors

    Hello everyone,

    I have recently purchased a house with a Brivis Buffalo 85 EMS gas ducted heating unit. Unfortunately I have no idea on how old the unit is as there was no documentation or instructions left when I moved in. Now that winter has arrived I have powered the unit on and I have been having some intermittent issues which I am hoping some of you could assist me with.

    The issues I am having are as follows;
    1. Poor airflow from all ducts
    2. Intermittent OH/F & OH/S errors on the control board


    This morning I awoke to a cold house and no air flowing from the ducts. I checked the unit and the fan was running however the burners and pilot light were off. The control board was showing an OH/F (overheat fan?) error. I reset the unit and the pilot light kicked in and lit the burners, the fan started and I went back inside. After a few minutes I again checked the ducts and again there was nothing coming out of them. Upon returning to the unit, the burners were out, fan was running and the OH/S error was showing on the control board.

    I'm trying to determine what is the likely cause of these errors? I can get to and replace the pilot burner easily if needed but I'm not sure if this will fix the problem. Having done some reading I think the flame rollout sensor might need replacing but I have no idea where to find this on my unit.

    Attached are photos of my unit. The control board is currently showing everything as green however the OH/F & OH/S errors are intermittent.

    Any help would be appreciated. Thanks.

    brivis-1.jpg
    Brivis Buffalo 85 EMS

    brivis-2.jpg
    Control Board

    brivis-3.jpg
    Wiring Diagram

    brivis-4.jpg
    Pilot Burner

  2. #2
    1K Club Member
    Join Date
    Nov 2011
    Location
    s.e. melb
    Posts
    1,867

    Default

    If it's shutting down due to o/h issues, try checking your return air filter behind the r/a grille, if blocked with dust, will cause low airflow and will overheat unit, causing it to shutdown. Also if possible check all ductwork for any damage. p.s. this model was subject to a recall by Brivis back in about 2000, which I was involved, ring Brivis to see if yours had the update. It was free at the time but they will charge you to do it now.

    Brivis Buffalo 85 EMS


    Control Board


    Wiring Diagram


    Pilot Burner[/QUOTE]


Similar Threads

  1. Brivis Buffalo 85 Problem
    By Chexfxdx in forum Heating & Cooling
    Replies: 26
    Last Post: 26th May 2013, 08:21 AM
  2. Questions regarding DIY install of Brivis Buffalo 20 ducted heating
    By johnstonfencing in forum Heating & Cooling
    Replies: 3
    Last Post: 17th Apr 2012, 08:32 PM
  3. Brivis buffalo 20 clicking noise
    By kman82 in forum Heating & Cooling
    Replies: 1
    Last Post: 16th Dec 2011, 01:05 AM
  4. RunTime Errors on the BB
    By vsquizz in forum Feedback & Help
    Replies: 7
    Last Post: 30th Aug 2004, 12:48 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •