Mini orb on wall behind wood heater

Results 1 to 26 of 26
  1. #1
    Novice
    Join Date
    May 2012
    Location
    Northern NSW
    Posts
    43

    Default Mini orb on wall behind wood heater

    I am new to renovating but both myself and my partner are obsessed by the idea of framing mini orb on the walls behind the wood heater that will sit on a slate hearth in a corner of the lounge room. I haven't been able to find much info about it on the internet other than it is advised to leave room between the mini orb and the wall for air flow. Is there anyone who could give me any more information?

  2. #2
    4K Club Member
    Join Date
    Nov 2009
    Location
    Geelong
    Posts
    6,297

    Default

    Seen this done many times, first response is always to ask you local council to see if they have any specific requirements but in one friends house she had to use cement sheet behind and against the wall with vertical steel "U" or "Z" brackets, the mini-orb screwed to the brackets and a 25mm air-gap between the cement sheet and the mini orb and all the way, floor to the ceiling. from memory the gap at floor and ceiling was also 25mm to allow the air to move ( it was single skin flue and it was a while ago- these days I think a double skin flue is the minimum) and the gap had a layer gal steel angle against the sheet on the wall.

    I have seen similar installations where two layers of steel were required by council, each with a 25mm air-gap, the first steel sheet usually flat plate and often decorative pierced plate used as the second, visible shield.
    I love the look of these myself and I'm trying to convince the Minister of War and Finance to plan a wood fire for our extension.

  3. #3
    Resigned SilentButDeadly's Avatar
    Join Date
    Sep 2006
    Location
    Not here...
    Posts
    5,155

    Default

    Moondog has it fine. Basically you fit Rondo furring channel to the wall behind the fireplace and attach the miniorb to that with wafer head screws. Top or frame out out the wall with a metal flashing to suit and you are done.
    Joined RF in 2006...Resigned in 2020.

  4. #4
    1K Club Member
    Join Date
    Nov 2008
    Location
    Sydney
    Posts
    1,108

    Default

    Just looking at the BCA, and it states where a heat shield is used it must not be less than 90mm masonry. It should rise 600mm min above the top of the unit and have a 25mm gap between the existing wall and the masonry wall and a 50mm gap between heat shield and unit

    So would put up a masonry wall first then fix sheets to that

  5. #5
    4K Club Member
    Join Date
    Nov 2009
    Location
    Geelong
    Posts
    6,297

    Default

    Not sure that's right Cherub, there must be deemed to satisfy provisions for alternative construction hidden in there somewhere, otherwise we could not use compressed sheet underneath the buggers.
    There would be absolutely no point in using both masonry and metal.
    I know I would be happy with double layer steel heat-shields myself with even the most basic of pot bellys but i would also not want to quibble with an insurance company trying to weasel out of a claim

  6. #6
    4K Club Member
    Join Date
    Nov 2009
    Location
    Geelong
    Posts
    6,297

    Default

    http://www.sustainability.vic.gov.au...od_heating.pdf

    Heat shields
    The distance required between a wood heater and a plaster or wooden wall can be safely reduced by the use of correctly installed heat shields. Heat shields may be constructed from brick, metal, high-temperature fibreboard or a proprietary heat shield material. In all cases a ventilated or air gap must be left between the heat shield and the wall.

    that is the Victorian view at the moment as far as I can tell

  7. #7
    1K Club Member
    Join Date
    Nov 2008
    Location
    Sydney
    Posts
    1,108

    Default

    Would check through AS 2918 for confirmation on substitutes. Will try to dig it up later

  8. #8
    Hammer Head - 1K Club Member
    Join Date
    Jan 2005
    Location
    Sydney
    Posts
    2,429

    Default

    Fc sheet is normal not sufficient to provide fire rating, you will need a wall system of fire rated plasterboard ie 2 layers 13mm = 2hr or a fire rated board light promat makes.

  9. #9
    4K Club Member
    Join Date
    Nov 2009
    Location
    Geelong
    Posts
    6,297

    Default Congrats to SBD

    I just noticed that SilentButDeadly has hit his second millennium with 2000 posts. Break out the bubbly and party

  10. #10
    4K Club Member
    Join Date
    Nov 2009
    Location
    Geelong
    Posts
    6,297

    Default

    But we are not talking about a fire rated wall.
    Anyway fire rated plaster is only rated for ceiling use, had that particular issue in another life. Although i think there are some new products that are designed for walls, need to double check.
    Heat shields are used to lower the allowable distance between a hazard (wood stove) and a combustible wall.

    I have seen literally dozens of wood stoves installed with-in 100mm of a timber stud and plaster wall using a double steel heat-shield with air gaps, never heard on any of them burning down accidentally except in bushfire, so I would say it was safe.
    Perhaps the standards have become tighter, but that is not necessarily to say the old standards were unsafe.

    If it were my wall I would specify Compressed sheet and be very happy, 13mm compressed cement sheet is very heat resistant, not to be confused with ordinary cement sheeting like Hardieboard

  11. #11
    4K Club Member
    Join Date
    Nov 2009
    Location
    Geelong
    Posts
    6,297

    Default

    Under the Building Code of Australia Compressed
    Fibre Cement sheeting is deemed to be non-combustible.
    When tested in accordance with Australian Standard AS
    1530.3 the Early Fire Hazard Indices are as follows:
    Ignitability Index 0
    Spread of Flame Index 0
    Heat Evolved Index 0
    Smoke Developed Index 0 1

    Cut and pasted from the BCG website

  12. #12
    Hammer Head - 1K Club Member
    Join Date
    Jan 2005
    Location
    Sydney
    Posts
    2,429

    Default

    Quote Originally Posted by Moondog55 View Post
    But we are not talking about a fire rated wall.
    Anyway fire rated plaster is only rated for ceiling use, had that particular issue in another life. Although i think there are some new products that are designed for walls, need to double check

    If it were my wall I would specify Compressed sheet and be very happy, 13mm compressed cement sheet is very heat resistant, not to be confused with ordinary cement sheeting like Hardieboard
    Incorrect normal fire rated p/b can be used for walls or ceilings,
    compressed fibro does have fire ristant properties but fire rated plasterboard is cheaper even if you need two layers.


    You will need to check that 12mm Cfc is suitable.

  13. #13
    4K Club Member
    Join Date
    Nov 2009
    Location
    Geelong
    Posts
    6,297

    Default

    Gaza I refer you back to post #11

  14. #14
    Hammer Head - 1K Club Member
    Join Date
    Jan 2005
    Location
    Sydney
    Posts
    2,429

    Default

    Quote Originally Posted by Moondog55 View Post
    Gaza I refer you back to post #11
    Does not rate to fire rating in terms of mins. Only flame transfer ie will nnot catch on fire but will allow thermal transfer. Plywood also can be found that has low flame index. Some timbers ie ironbArk very low flame index.

    Under BCA it sets out the requirements as

    Structural adequacy / Intergity / insulation.

    For eg a 2hr fire rated wall system is two layers 13mm fire check each side of the studs.

  15. #15
    4K Club Member
    Join Date
    Nov 2009
    Location
    Geelong
    Posts
    6,297

    Default

    Sorry GAZA but you have lost me on this one.
    In the application we are talking about a wall is either flammable or not.
    The question was about heat shields in front of flammable walls and we seem to have got side tracked. I think I'm going to call my local council and see what the Greater Geelong position is as this is something we need to fund if we decide to go with a wood fire ourselves

  16. #16
    4K Club Member
    Join Date
    Nov 2009
    Location
    Geelong
    Posts
    6,297

    Default

    Well I just got off the phone with the Geelong building section.
    New BCA documents were released on 01 May and they do not yet have copies, old standard was a 90mm masonry wall with 25mm air-gap which is pointless, you may as well just build a masonry wall.
    Lovely woman is going to send me photo copies of the new document as soon as they arrive, what she did tell me tho is; as long as the fireplace is installed in accordance with manufacturers instructions it is OK and the ripple iron would be just a decoration, clearances would be to the original wall not to the ripple iron surface.
    This woman just spent 20 minutes looking through the BCAs trying to find a definition of what constitutes a "combustible wall/surface" without luck and ditto for "non-combustible" wall and I thanked her for her effort.

    How are inspectors supposed to do their job properly if the information in the regulations is so hard to find??

  17. #17
    2K Club Member
    Join Date
    May 2011
    Location
    Melbourne south east
    Posts
    2,103

    Default

    I'm getting a little confused here. I have a freestanding wood heater installed two years ago. I just got out the

    installation instructions from the manufacturer ( Australian) which state that the fire box to comply with AS etc etc

    must be installed a minimum of 150mm from a combustible wall surface at the rear and 300mm at the side

    and if placed diagonally across a corner the two back corners must be a min. of 75mm from a combustible wall

    surface. If the wall is lined with mini orb why should this change?

    Just read your last post Moondog which seems to state that it doesn't

  18. #18
    4K Club Member
    Join Date
    Nov 2009
    Location
    Geelong
    Posts
    6,297

    Default

    hi goldie 1
    The point of a heat shield was to be able to reduce clearances.
    It seems as if the BCA has gone thru a few changes so rapidly that some sections do not make a lot of sense.
    Just imagine tho that you had an antique pot belly stove you wanted to install in your lounge room, and to be compliant it needed 1500mm or more of clearance to a "Combustible wall" the use of heat shields should be able to reduce that distance to 100mm or so.
    The OP can do whatever they like if they keep to the manufacturers installation instructions as the ripple iron is considered "Decoration" but it was common practice to use dual layers of steel sheet with dual 25mm air gaps when installing wood heaters.
    Heat-sheilds work in the same way as the newer "Zero clearance" wood heaters; an air-wash keeps the outer skin of the heater from getting too hot by a combination of convective and radiative cooling, a heat shield keeps the inner skin , the one next to the combustible wall, cool from the same mechanism.

  19. #19
    2K Club Member
    Join Date
    May 2011
    Location
    Melbourne south east
    Posts
    2,103

    Default

    Understood. Thanks

  20. #20
    1K Club Member
    Join Date
    Nov 2008
    Location
    Sydney
    Posts
    1,108

    Default

    Don't worry about the BCA to much, you need the AS/NZS 2918 [sorry cant find it].

    Clearances for different materials are determined by testing in this standard, Then BCA minimums are used if not using AS

  21. #21
    4K Club Member
    Join Date
    Nov 2009
    Location
    Geelong
    Posts
    6,297

    Default

    I have a very real problem with forking out that amount of hard earned cash just to do a little research on feasibility, like most on the forum I feel that if compliance with a standard is mandatory the information should be available FOC.

  22. #22
    1K Club Member
    Join Date
    Nov 2008
    Location
    Sydney
    Posts
    1,108

    Default

    I'm hearing you, we fork out considerable amounts of money just to keep up to date. Tradespeople at least should have access to relevant information to perform there jobs to the standards.

  23. #23
    7K Club Member
    Join Date
    Jun 2010
    Location
    Geelong
    Posts
    7,921

    Default

    I've been following this one for a while, and it seemed logical that the box manufacturer is the one who needs to provide relevant clearance info in the installation guide, as they are the only ones who know how their boxes are built

  24. #24
    4K Club Member
    Join Date
    Nov 2009
    Location
    Geelong
    Posts
    6,297

    Default

    While it may seem logical, sometimes the space available isn't there, that was and is the whole point of the low profile heat shields, sacrifice 50mm of wall space to gain 550mm of room space. Made sense and it worked

    This is one rule ( the 90mm masonry heat shield ) that simply makes no sense, OK I don't have access to the relevant Australian standard ( they cost too much money to buy ) but it seems like common sense and good building practice has been thrown out the doorway.
    It would help a lot if there was a definition and description of "Non-flammable" wall that could be understood by some-one who does not have a degree in engineering.
    No good having a performance based building standard if they won't tell you what the performance should be.

  25. #25
    Novice
    Join Date
    May 2012
    Location
    Northern NSW
    Posts
    43

    Default Response to post

    Wow. I just want to thank you all for your response to my post. I have found the information very useful.

  26. #26
    4K Club Member
    Join Date
    Nov 2009
    Location
    Geelong
    Posts
    6,297

    Default

    You probably got a lot more than you asked for, these threads and their daughter threads often take on a life of their own.
    Your pictures of the finished project are expected.

Similar Threads

  1. Wood heater removal
    By jmn in forum Heating & Cooling
    Replies: 11
    Last Post: 28th Apr 2012, 06:39 AM
  2. Base for wood heater
    By brettsyoung in forum Heating & Cooling
    Replies: 15
    Last Post: 15th Jul 2011, 02:50 PM
  3. Help - Mini earthquake on retaining wall!!
    By nelum in forum Retaining Walls
    Replies: 3
    Last Post: 10th Oct 2010, 10:46 AM
  4. Can Anyone Identify my wood heater
    By Sorceror in forum Heating & Cooling
    Replies: 19
    Last Post: 25th Aug 2010, 03:13 PM
  5. Toxic wood heater
    By henlan77 in forum General Odds & Sods
    Replies: 7
    Last Post: 20th Aug 2008, 02:18 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •