    For those who are unaware, the general recommendation when cutting or undoing metal water pipes or metal gas pipes is to use a jumper lead across the break or cut or disconnection so that if there is an earth or neutral fault in the electrical system that you don't get electrocuted.
    There is no middle ground between facts and fallacies - argumentum ad temperantiam

  3. #3
    ℱᎾℛUℳ ℂℒᎾᏇℕ PlatypusGardens's Avatar
    Join Date
    Oct 2011
    Location
    W👀MBYE
    Posts
    8,624

    Default

    Well.....how the hell are you supposed to avoid that.....?

    Workplace Health and Safety Queensland and the Electrical Safety Office are investigating a fatal electrical incident that happened on Sunday 9 October 2016 at Ayr.A man died after he received an electric shock while cutting a metal water pipe to repair a leak.


    First inspections revealed that the neutral line from the power pole to the house had come away from the pole and did not provide a return path from the house, instead the water pipe had become the return path.


    This alert is to remind you and your organisation to be safe around electricity.


    It says "A man"....so was he a licensed plumber or not......doesn't really matter when the electricity is running through the plumbing.....you'd be screwed regardless



    Accident free since yesterday



  4. #4
    2K Club Member
    Join Date
    Aug 2005
    Location
    brisbane . australia
    Posts
    2,166

    Default

    indeed..."This alert is to remind you and your organisation to be safe around electricity."..Duh.. well he wasnt playing with electricity..

  5. #5
    Community Moderator phild01's Avatar
    Join Date
    Aug 2009
    Location
    Sydney, north
    Posts
    16,458

    Default

    How common is it for that to happen at the pole?

  6. #6
    Community Moderator
    Join Date
    Dec 2008
    Location
    Queensland
    Posts
    7,793

    Default

    This happened in Ayr in NQ and the incident I was involved in happened at Giru 50 klm north. I wouldn't be surprised if it was a common occurrence.

  7. #7
    Community Moderator
    Join Date
    Dec 2008
    Location
    Queensland
    Posts
    7,793

    Default

    Quote Originally Posted by chrisp View Post
    For those who are unaware, the general recommendation when cutting or undoing metal water pipes or metal gas pipes is to use a jumper lead across the break or cut or disconnection so that if there is an earth or neutral fault in the electrical system that you don't get electrocuted.
    If you think about that recommendation you will realise how silly it is. You cut a pipe that is part of the return and you are left with a cable that is alive. The only way is turn off the main switch.

  8. #8
    3K Club Member
    Join Date
    Jun 2012
    Location
    Sunshine Coast
    Posts
    3,945

    Default

    Quote Originally Posted by Bros View Post
    If you think about that recommendation you will realise how silly it is. You cut a pipe that is part of the return and you are left with a cable that is alive. The only way is turn off the main switch.
    Then test to make sure there is absolutely no current at the pipe.

  9. #9
    4K Club Member Marc's Avatar
    Join Date
    Jul 2003
    Location
    Sydney
    Posts
    13,914

    Default

    So the earth is acting as neutral. That should trigger the safety switch right?
    Enjoy present pleasures in such a way as not to injure future ones.
    Seneca

  10. #10
    Community Moderator phild01's Avatar
    Join Date
    Aug 2009
    Location
    Sydney, north
    Posts
    16,458

    Default

    Quote Originally Posted by Marc View Post
    So the earth is acting as neutral. That should trigger the safety switch right?
    I think it needs neutral to know.

  11. #11
    Community Moderator
    Join Date
    Dec 2008
    Location
    Queensland
    Posts
    7,793

    Default

    Quote Originally Posted by cyclic View Post
    Then test to make sure there is absolutely no current at the pipe.
    Not putting plumbers down but it would be above their pay scale to test for current flow.

  12. #12
    Community Moderator
    Join Date
    Dec 2008
    Location
    Queensland
    Posts
    7,793

    Default

    Quote Originally Posted by Marc View Post
    So the earth is acting as neutral. That should trigger the safety switch right?
    No it won't as the neutral is before the RCD.

  13. #13
    ℱᎾℛUℳ ℂℒᎾᏇℕ PlatypusGardens's Avatar
    Join Date
    Oct 2011
    Location
    W👀MBYE
    Posts
    8,624

    Default

    Quote Originally Posted by Bros View Post
    Not putting plumbers down but it would be above their pay scale to test for current flow.

    Well....how often has this happened?
    Would any plumber out there ever check if a pipe is electrified before cutting it?


    Seriously...this is a freak accident.




    .....unless a licenesed sparky didn't do their job properly and didn't properly connect that cable which "came away".........


    .....huh...
    Accident free since yesterday



  14. #14
    Community Moderator
    Join Date
    Dec 2008
    Location
    Queensland
    Posts
    7,793

    Default

    There is another parallel path which should have saved him and that was the earth stake. The water pipe in only a bonding to bring the water pipes down to earth potential not as an earth return. The earth stake is the main earth and the water pipe should not have caused any problems. Obviously the house electrical system was substandard.

  15. #15
    2K Club Member chrisp's Avatar
    Join Date
    May 2004
    Location
    Melbourne, Australia
    Posts
    2,815

    Default

    Plumbers are trained during their apprenticeship years to connect bonding cables, typically battery jumper leads, across the water pipe point to be breached before all work is started.

    Quote from: Avoid electrical shocks when working with water supply mains - Environment and Planning Directorate - Planning
    There is no middle ground between facts and fallacies - argumentum ad temperantiam

  16. #16
    4K Club Member ringtail's Avatar
    Join Date
    Sep 2009
    Location
    brisbane
    Posts
    8,266

    Default

    Quote Originally Posted by chrisp View Post
    Plumbers are trained during their apprenticeship years to connect bonding cables, typically battery jumper leads, across the water pipe point to be breached before all work is started.
    Have never and dare I say will never see a plumber (or anyone else) do that.

  17. #17
    2K Club Member chrisp's Avatar
    Join Date
    May 2004
    Location
    Melbourne, Australia
    Posts
    2,815

    Default

    Quote Originally Posted by Bros View Post
    There is another parallel path which should have saved him and that was the earth stake. The water pipe in only a bonding to bring the water pipes down to earth potential not as an earth return. The earth stake is the main earth and the water pipe should not have caused any problems. Obviously the house electrical system was substandard.
    Correct - it is probably two faults that caused the death - but it happens.
    There is no middle ground between facts and fallacies - argumentum ad temperantiam

  18. #18
    4K Club Member Marc's Avatar
    Join Date
    Jul 2003
    Location
    Sydney
    Posts
    13,914

    Default

    Quote Originally Posted by ringtail View Post
    Have never and dare I say will never see a plumber (or anyone else) do that.
    My son in law came to do some work when we did the bathroom renovation and I saw him earthing the old pipework before cutting it.
    Enjoy present pleasures in such a way as not to injure future ones.
    Seneca

  19. #19
    2K Club Member chrisp's Avatar
    Join Date
    May 2004
    Location
    Melbourne, Australia
    Posts
    2,815

    Default

    Quote Originally Posted by ringtail View Post
    Have never and dare I say will never see a plumber (or anyone else) do that.
    I'd hazard to guess that they don't bother wearing seat belts when they drive either - same difference!
    There is no middle ground between facts and fallacies - argumentum ad temperantiam

  20. #20
    2K Club Member chrisp's Avatar
    Join Date
    May 2004
    Location
    Melbourne, Australia
    Posts
    2,815

    Default

    Quote Originally Posted by PlatypusGardens View Post
    Well....how often has this happened?
    Would any plumber out there ever check if a pipe is electrified before cutting it?


    Seriously...this is a freak accident.

    Yep, it's a freak accident but they do happen. It is interesting to look at some of the statistics (which I haven't done for a few years!). IIRC, mechanics were the most likely to be killed by having a jack fail and have a car crush them; while the numbers are somewhat patchy, electricians seem to be the most likely to be electrocuted.

    I suppose we all become complacent and can get caught out.

    Anyway, please be careful out there!
    There is no middle ground between facts and fallacies - argumentum ad temperantiam

  21. #21
    Member
    Join Date
    Aug 2014
    Location
    Victoria
    Posts
    80

    Default

    Quote Originally Posted by Bros View Post
    There is another parallel path which should have saved him and that was the earth stake.
    Older installations never had an earth stake. They used the copper water pipe bond as the main earth.
    I know plenty of plumbers who have got tingles of pipes when they cut them and don't understand why. It's just not something many people immediately think about.

  22. #22
    Golden Member
    Join Date
    Aug 2012
    Location
    Sydney
    Posts
    618

    Default

    The jumper lead bridging the cut pipe is a great idea. Sure the jaws would be live but pose a much lower risk than the 2 ends of a cut pipe 3mm apart. I bet most plumbers carry one but rarely use it.
    If the earth stake was going into dry ground the water pipe would have much lower resistance so carry most of the current.

  23. #23
    1K Club Member Spottiswoode's Avatar
    Join Date
    Sep 2015
    Location
    Lake Macquarie
    Posts
    1,009

    Default

    I remember hearing about this year's ago, probably in an electrical safety course. It was not long after I had disconnected the water meter at home trying to fix a leak. Scared me a bit at the time, just hope that in the future I still remember it if I need to cut the 'circuit' again.
    Measure twice, cut once, trim some off the end, trim some more. Too short. Rinse, Repeat.

  24. #24
    ℱᎾℛUℳ ℂℒᎾᏇℕ PlatypusGardens's Avatar
    Join Date
    Oct 2011
    Location
    W👀MBYE
    Posts
    8,624

    Default

    Quote Originally Posted by chrisp View Post
    ......electricians seem to be the most likely to be electrocuted......

    .....and I'm not surprised.


    The amount of sparkies I've seen [s]play[/s] work with live wires hooking up a switch or GPO......
    Accident free since yesterday



  25. #25
    ℱᎾℛUℳ ℂℒᎾᏇℕ PlatypusGardens's Avatar
    Join Date
    Oct 2011
    Location
    W👀MBYE
    Posts
    8,624

    Default

    Quote Originally Posted by Muzza40 View Post
    Older installations never had an earth stake. They used the copper water pipe bond as the main earth.
    I know plenty of plumbers who have got tingles of pipes when they cut them and don't understand why. It's just not something many people immediately think about.

    I often get tingles from taps especially if I have a cut on my hands/fingers
    Accident free since yesterday



  26. #26
    2K Club Member chrisp's Avatar
    Join Date
    May 2004
    Location
    Melbourne, Australia
    Posts
    2,815

    Default

    Quote Originally Posted by PlatypusGardens View Post
    I often get tingles from taps especially if I have a cut on my hands/fingers
    Check your equipotential bond. It's a wire that 'bonds' the plumbing to the electrical earth.
    There is no middle ground between facts and fallacies - argumentum ad temperantiam

  27. #27
    Member
    Join Date
    Aug 2014
    Location
    Victoria
    Posts
    80

    Default

    I'd be checking the neutral first.

  28. #28
    4K Club Member ringtail's Avatar
    Join Date
    Sep 2009
    Location
    brisbane
    Posts
    8,266

    Default

    Quote Originally Posted by chrisp View Post
    I'd hazard to guess that they don't bother wearing seat belts when they drive either - same difference!
    Yep.

  29. #29
    4K Club Member ringtail's Avatar
    Join Date
    Sep 2009
    Location
    brisbane
    Posts
    8,266

    Default

    Quote Originally Posted by chrisp View Post
    Check your equipotential bond. It's a wire that 'bonds' the plumbing to the electrical earth.
    Just re did mine a few months back. Copper pipe was painted and the clamp was also painted. Got my sparky to check and while he was there doing other stuff Polished up the pipe and clamp. Sparky rechecked before he left. All good and one less thing to worry about.

  30. #30
    ℱᎾℛUℳ ℂℒᎾᏇℕ PlatypusGardens's Avatar
    Join Date
    Oct 2011
    Location
    W👀MBYE
    Posts
    8,624

    Default

    Quote Originally Posted by chrisp View Post
    Check your equipotential bond. It's a wire that 'bonds' the plumbing to the electrical earth.

    Wasn't talking about my place specifically....more in general.
    Seems to happen to me more than others too.

    Guess I'm more....conductive than some

    Accident free since yesterday



  31. #31
    Community Moderator
    Join Date
    Dec 2008
    Location
    Queensland
    Posts
    7,793

    Default

    Quote Originally Posted by PlatypusGardens View Post
    Wasn't talking about my place specifically....more in general.
    Seems to happen to me more than others too.

    Guess I'm more....conductive than some

    Happens to me as well but only on a cut finger. The skin seems to act as an insulator compared to raw tissue. I have never measured it but I believe it would be very very low voltage. I would only expect that to happen in a slab on ground shower.

  32. #32
    Community Moderator
    Join Date
    Dec 2008
    Location
    Queensland
    Posts
    7,793

    Default

    With the unfortunate incident rare though it is there were two faults that contributed to the fatality. Loss of neutral at the service pole (seen two of them)and lack of effective earth stake. The plumber could not have known this but I bet the householder did know there was a problem but couldn't explain it.

    As for fitting a bridge around the cut seems fine in theory but you have to disconnect the clamp and if you disconnect the end that goes to the ground first the clamp is alive and how many clamps in a plumbers truck would be insulated. Doing the repair it could be a nuisance working around the bridge and its integrity could be comprised.

    This incident is rare and I will be interested to see the coroners report for the full details.

  33. #33
    Member
    Join Date
    May 2014
    Location
    Adelaide
    Posts
    92

    Default

    Have been renovating off and on a few years now and will put my hand to most things. Know a good plumber and a good electrician. Do lots of the prep work for them, but I do what they say and pay their bills straight away. Sounds like I might be on to something.......

Similar Threads

  1. Distance between plumbing and electrical
    By webtubbs in forum Electrical
    Replies: 8
    Last Post: 29th May 2016, 10:50 PM
  2. Replies: 3
    Last Post: 3rd May 2012, 09:15 PM
  3. Plumbing & Electrical compliance certificates
    By Border boy in forum Plumbing
    Replies: 9
    Last Post: 25th Jan 2009, 11:49 AM
  4. Roughing in electrical/plumbing in slab
    By Ashes1 in forum Electrical