Water Contamination with Black Specs

Results 1 to 19 of 19
  1. #1
    Novice
    Join Date
    Nov 2013
    Location
    Melbourne
    Posts
    33

    Question Water Contamination with Black Specs

    Hi there.
    Not sure what is going here, but I noticed a load of black particles coming out of the hot water (shower and taps).

    Initially I thought could be something wrong with the head shower, but then I noticed I found the same particulate on different taps around the house.

    I have four assumptions:
    1) The hydronic panels are releasing the foreign material (read below)
    2) The Rinnai 200e (heat source) is releasing the particulate
    3) The Grundfos Pump (hydronic pump) is releasing the particulate.
    4) The pipes are corroded (I thought they were made of copper) but I have to consider that as well.

    I bought my house with the current how water + hydronic system. So apart from who installed it - there is a sticker in the pump enclosure - I don't have the plumbing diagrams that shows what was installed here.

    All I know (that is explicitly advertised on their website as well) is the hydronic loop and hot water loop are the same thing. Which adds even more complexity to this problem.

    During the reno, the panels were removed to paint the walls behind them, and we noticed that a considerably high amount of heavy particulate was coming out of the radiators while bleeding them.

    I attached two images, one with the baby bath showing the black particulate (it's metal for sure) and another one with the system architecture from the installer (I removed the company logo as I don't want to roast them here).

    To the specialists here, have you ever seen this?

    Maybe the plumbing code has changed (correct me if I'm wrong please) but I would imagine these two systems should work on separate loops (?) - Maybe this is a separate issue, but that made me think about this...

    hydronic.jpgimg_7288.jpg

    Any comment/thought would be great, I'm really concerned about this.

  2. #2
    1K Club Member
    Join Date
    Nov 2011
    Location
    Paradise Beach Vic
    Posts
    1,875

    Default

    Rule out your hydronic, that will be a sealed loop with an air gap to avoid cross connection. Run all taps for a minute to see if it clears. Could be either crap thats come through from the mains or even a water filter may have crapped itself.
    Love it when DIYERS pin the blame on plumbers for their own shoddy work

  3. #3
    Novice
    Join Date
    Nov 2013
    Location
    Melbourne
    Posts
    33

    Default Water Contamination with Black Specs

    Quote Originally Posted by plum View Post
    Rule out your hydronic, that will be a sealed loop with an air gap to avoid cross connection. Run all taps for a minute to see if it clears. Could be either crap thats come through from the mains or even a water filter may have crapped itself.
    Thanks plum. But I did not understand your statement about the sealed loop. I can guarantee you they are in the same loop here, there is cross connection for sure and I can’t isolate the hydronic.
    I’ll try your method tough


    S

  4. #4
    3K Club Member
    Join Date
    Jun 2012
    Location
    Sunshine Coast
    Posts
    3,937

    Default

    CAUTION OP

    I strongly suggest you contact the design company or someone who is familiar with these systems as you may be dealing with LEGIONNAIRES due to dead legs (pipes not used very often)


    Plum

    Not about to go against your up to date expertise as I have never had anything to do with hydronic heating, but what I see in the diagram is a simple flow return hot water system which feeds through

    the radiators in each room, but is also the supply return for the domestic hot water for showers etc.

    (see box on right of pic which shows "Water flow to radiators and domestic hot water fixtures."

    So I have to believe this is all one system.

    The particles could be coming from copper pipe which is not used very often or from the radiators, so flushing the system as you have suggested, making sure all radiators and hot taps are operated for

    a period of time , is the best idea.



    OP SEE MY CAUTION

  5. #5
    Resigned SilentButDeadly's Avatar
    Join Date
    Sep 2006
    Location
    Not here...
    Posts
    5,155

    Default Water Contamination with Black Specs

    That looks like granulated carbon from a cartridge filter like my house setup pictured below.

    If you have something like this then it may have a loose fill carbon filter in the second housing that has failed...
    Joined RF in 2006...Resigned in 2020.

  6. #6
    4K Club Member
    Join Date
    Jan 2014
    Location
    Kangaroo Island
    Posts
    4,513

    Default

    The particles look like corrosion from copper within the system (disclaimer - I am not an expert). What is the source of water used in your house? Rainwater is becoming increasing corrosive in copper pipes due to the rise in atmospheric CO2. I solved corrosion problems in a previous house running rainwater by dropping limestone rocks in each tank which raised the pH from 6.2 to 6.8. Desalinated water is also corrosive in copper plumbing unless it is re-mineralised.

    Edit: acidic corrosion increases as temperature increases, so I would expect corrosion will appear in hot water circuits first.
    Before you speak, ask yourself: Is it necessary, it is true, does it improve on the silence? - Baba

  7. #7
    Novice
    Join Date
    Nov 2013
    Location
    Melbourne
    Posts
    33

    Default

    Thanks SilentButDeadly, but my house is not fitted with any filter.

  8. #8
    Novice
    Join Date
    Nov 2013
    Location
    Melbourne
    Posts
    33

    Default

    Water is coming from the main water supply, from Yarra Valley.
    You gave me a good idea now, I should check the first tap just after the meter, and see if there are particles coming from there.

    Quote Originally Posted by John2b View Post
    The particles look like corrosion from copper within the system (disclaimer - I am not an expert). What is the source of water used in your house? Rainwater is becoming increasing corrosive in copper pipes due to the rise in atmospheric CO2. I solved corrosion problems in a previous house running rainwater by dropping limestone rocks in each tank which raised the pH from 6.2 to 6.8. Desalinated water is also corrosive in copper plumbing unless it is re-mineralised.

    Edit: acidic corrosion increases as temperature increases, so I would expect corrosion will appear in hot water circuits first.

  9. #9
    Novice
    Join Date
    Nov 2013
    Location
    Melbourne
    Posts
    33

    Default

    It is all in one system. Guaranteed.

    I took the Hydronic enclosure cover off and check this out (check all images, they are from looking downwards to upwards, towards the boiler).



    It is a one loop system for sure.


    Quote Originally Posted by cyclic View Post
    CAUTION OP

    I strongly suggest you contact the design company or someone who is familiar with these systems as you may be dealing with LEGIONNAIRES due to dead legs (pipes not used very often)


    Plum

    Not about to go against your up to date expertise as I have never had anything to do with hydronic heating, but what I see in the diagram is a simple flow return hot water system which feeds through

    the radiators in each room, but is also the supply return for the domestic hot water for showers etc.

    (see box on right of pic which shows "Water flow to radiators and domestic hot water fixtures."

    So I have to believe this is all one system.

    The particles could be coming from copper pipe which is not used very often or from the radiators, so flushing the system as you have suggested, making sure all radiators and hot taps are operated for

    a period of time , is the best idea.



    OP SEE MY CAUTION
    Attached Thumbnails Attached Thumbnails image02.png   image03.png   image01.png  

  10. #10
    4K Club Member
    Join Date
    Jan 2014
    Location
    Kangaroo Island
    Posts
    4,513

    Default

    How does the hot water in the first picture pipe 'D' get to the heater in the second picture with the circulation pump, which is driving the hydronic heating? Or does pipe 'D' go to the second bathroom and laundry?
    Before you speak, ask yourself: Is it necessary, it is true, does it improve on the silence? - Baba

  11. #11
    Novice
    Join Date
    Nov 2013
    Location
    Melbourne
    Posts
    33

    Default

    When the circulation pump is ON, it moves the water from the Pipe E to the boiler (it goes up in the picture), forcing the water to flow around the whole hydronic system. At the same time, the hot water coming out of the boiler finds its way to the pipe D (down in the picture). This is how the water flows in these two pipes.

    Just look at E and D pipes, ignoring all the rest, it will be easier to understand. I hope I clarified.

    Cheers.

    Quote Originally Posted by John2b View Post
    How does the hot water in the first picture pipe 'D' get to the heater in the second picture with the circulation pump, which is driving the hydronic heating? Or does pipe 'D' go to the second bathroom and laundry?

  12. #12
    4K Club Member
    Join Date
    Jan 2014
    Location
    Kangaroo Island
    Posts
    4,513

    Default

    So picture 1 joins under picture 2?
    Before you speak, ask yourself: Is it necessary, it is true, does it improve on the silence? - Baba

  13. #13
    Novice
    Join Date
    Nov 2013
    Location
    Melbourne
    Posts
    33

    Default Water Contamination with Black Specs

    Quote Originally Posted by John2b View Post
    So picture 1 joins under picture 2?
    Yes


    S

  14. #14
    1K Club Member
    Join Date
    Nov 2011
    Location
    Paradise Beach Vic
    Posts
    1,875

    Default

    Quote Originally Posted by cyclic View Post
    CAUTION OP

    I strongly suggest you contact the design company or someone who is familiar with these systems as you may be dealing with LEGIONNAIRES due to dead legs (pipes not used very often)


    Plum

    Not about to go against your up to date expertise as I have never had anything to do with hydronic heating, but what I see in the diagram is a simple flow return hot water system which feeds through

    the radiators in each room, but is also the supply return for the domestic hot water for showers etc.

    (see box on right of pic which shows "Water flow to radiators and domestic hot water fixtures."

    So I have to believe this is all one system.

    The particles could be coming from copper pipe which is not used very often or from the radiators, so flushing the system as you have suggested, making sure all radiators and hot taps are operated for

    a period of time , is the best idea.



    OP SEE MY CAUTION
    Certainly have more knowledge of the older hydronics which had header tanks to top the system up with a physical air break. It appears this system has non-return valves, like a reduced pressure zone valve to stop heating water entering the domestic hot water supply.

    As you suggest, best the experts look at this.
    Love it when DIYERS pin the blame on plumbers for their own shoddy work

  15. #15
    Novice
    Join Date
    Nov 2013
    Location
    Melbourne
    Posts
    33

    Default Water Contamination with Black Specs

    Long time since my last post, but between my first post and today I have not only trying to make a positive contact with the company that supplied the system but trying to find a plumber experienced on this system. I failed badly ��

    Firstly, I am convinced this system is a lemon.

    I contacted the system seller, but I could not get too far. According to them the system is watermark as all hardware supplied is copper. But himself advised me to flush/clean the system every year (it cost $700 per year). So I failed to follow his logic! If the system is really clean why bother flushing it every year? I gave up. The guy over the phone was rude and he was blaming the main water service for the gunk.

    I got VBA onboard as well to seek some help, they were extremely helpful but they could not find who actually installed the system. So even we know who supplied the system there is no document showing us who installed this crap here.

    So at the moment I’m fully convinced that I need to split this system in two and move forward.

    To achieve that i will be installing a 2nd heating unit/boiler and split the system. The only issue is ensuring the water service is now fully isolated from the old hidronic loop. But I reckon any experienced plumber can do that. At the moment under my bathroom floor there are some dodgy plumbing happening as my local plumber could not isolate the loops.

    Thanks for all suggestions and I’ll keep posting


    Sent

  16. #16
    Senior Member
    Join Date
    Nov 2013
    Location
    Vic
    Posts
    297

    Default

    Suspect the supplier to be H****T**** and the system classed as G****H***.
    If you check the temperature at the hot water kitchen tap it will give you an indication at what the rinnai unit is set to.
    The bathroom & ensuite, being ablution fixtures, should have temperature of no greater than 50 degrees C.
    The only way to achieve this in a system of this nature is with tempering valves.
    Therefore the presumption is that one is fitted somewhere along pipeline 'C' in pic 1 of #9.
    If the bathroom tees off from 'D' (flow line) then an additional tempering valve would be necessary.
    If the entire system is constructed from copper with welded (silver soldered) joints, then the particulates may well be carbon deposits from the welding process.
    If this is the case, then in hindsight you should have flushed out the panels before reinstalling them.

  17. #17
    Senior Member
    Join Date
    Apr 2018
    Location
    Western Australia
    Posts
    434

    Default

    I assume after this time the particles have stopped?
    Any low flow system like the hydronic heating will build up some settlement over time especially if not flushed properly initially. Even on town water it can be surprising what comes through.
    Since it's a common system using the same boiler when you disturbed it there has been some contamination of the hot water lines.

    My Old man's system is pretty similar but the equivalent to line "E" has a T off and a drain valve to give it a flush/remove air.

  18. #18
    Novice
    Join Date
    Nov 2013
    Location
    Melbourne
    Posts
    33

    Default

    Hi. correct.
    Rinnai is set to 65. And all taps and showers got hot water temp at this temp. Kids bath time is a nightmare for me as I need to supervise them all the time. The only good thing is having lava hot water at the kitchen to wash off grease and roasting trays.


    Quote Originally Posted by RodEye View Post
    Suspect the supplier to be H****T**** and the system classed as G****H***.
    If you check the temperature at the hot water kitchen tap it will give you an indication at what the rinnai unit is set to.
    The bathroom & ensuite, being ablution fixtures, should have temperature of no greater than 50 degrees C.
    The only way to achieve this in a system of this nature is with tempering valves.
    Therefore the presumption is that one is fitted somewhere along pipeline 'C' in pic 1 of #9.
    If the bathroom tees off from 'D' (flow line) then an additional tempering valve would be necessary.
    If the entire system is constructed from copper with welded (silver soldered) joints, then the particulates may well be carbon deposits from the welding process.
    If this is the case, then in hindsight you should have flushed out the panels before reinstalling them.

  19. #19
    Novice
    Join Date
    Nov 2013
    Location
    Melbourne
    Posts
    33

    Default

    Actually no. The system was pretty much turned off since October since the temperatures went up a bit in Melbourne.

    Interesting enough, on Sunday I was staring at this crap system, I had the idea to test if that check valve was doing its job.

    I've shut the valve A (hot water service) and tested if the hot tap would have any water.
    image01.png
    Looking at the below diagram, the check valve should not let any water flow back following the blue arrow, but for my surprise, the hot water tap was still flowing water suggesting the check valve was not working.
    image02.png
    The amount of crap that came out of the tap was amazing. I had to remove the aerator otherwise the were no flow. I let the water running for long time and it did flush a lot of crap.

    I removed the check valve and noticed the flap was indeed stuck - always open...I cleaned the flap shaft with a natural degreaser I had here around and the flap is now working as designed.

    We had several occasions of not having hot water (just lukewarm) and that was the issue, was the check valve letting cold water mixing with how water....

    Anyway, interesting trouble shouting and something to keep me busy during the lock down.

    For anyone thinking about this system, please stay away. There are so many design flaws and the failure mode impacts directly on your family health.

Similar Threads

  1. Strawberry Contamination
    By METRIX in forum At the end of the day
    Replies: 13
    Last Post: 24th Sep 2018, 08:43 PM
  2. Replies: 16
    Last Post: 26th May 2016, 08:12 PM
  3. Replies: 14
    Last Post: 17th Mar 2016, 09:21 PM
  4. Water Damage in Bathroom.. Possibly black mold?
    By eleanormichalka in forum Bathrooms
    Replies: 3
    Last Post: 16th Apr 2012, 12:57 PM
  5. Black Japan or Black Stain
    By mote in forum Flooring
    Replies: 2
    Last Post: 7th Apr 2006, 12:18 AM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •