    Default Generator question

    I've just made up a generator from an old Asian el Cheapo 13 HP Honda copy motor and a Honda 4 KVA generator. My problem is that I seem to have to run the motor at high revs to get up to 50 HZ. The pully was taken from the old motor (Honda 9HP) so the ratio is the same.

    Do all generator motors have to run at high revs to run at 50 HZ? I know I can use a smaller pully on the motor, but it's not easy. How much damage can I do running at, say, 40 HZ, which it does easily?

  2. #2
    Registered User
    Join Date
    Sep 2007
    Location
    Nowhere
    Posts
    638

    Default

    Quote Originally Posted by Rossluck View Post
    I've just made up a generator from an old Asian el Cheapo 13 HP Honda copy motor and a Honda 4 KVA generator. My problem is that I seem to have to run the motor at high revs to get up to 50 HZ. The pully was taken from the old motor (Honda 9HP) so the ratio is the same.

    Do all generator motors have to run at high revs to run at 50 HZ? I know I can use a smaller pully on the motor, but it's not easy. How much damage can I do running at, say, 40 HZ, which it does easily?
    A 2 pole generator (alternator) will need to rotate at a higher RPM than a 4 pole unit. How many poles does your generator have?

    Yes, you can damage some equipment by operating them at 40Hz. I would highly recommend that you try to achieve 50Hz.

  3. #3
    A Member of the Holy Trinity echnidna's Avatar
    Join Date
    Feb 2003
    Location
    Timboon VIC AUSTRALIA
    Posts
    2,746

    Default

    If you are only running brush type motors it won't make much difference.
    But if you want to run induction motors you should get it up to 50Hz.

    If it runs easily at 40 Hz use a pulley 25% larger and it should run 50Hz easily.
    Regards
    Bob Thomas

    ==================================
    Ebooks For Sale

    Doll House Book Shelf PLANS

  4. #4
    Registered User
    Join Date
    Sep 2007
    Location
    Nowhere
    Posts
    638

    Default

    Quote Originally Posted by echnidna View Post
    If you are only running brush type motors it won't make much difference.
    But if you want to run induction motors you should get it up to 50Hz.

    If it runs easily at 40 Hz use a pulley 25% larger and it should run 50Hz easily.
    Just curious Bob, what's the difference you are talking about?


    To produce 50Hz, the following applies;

    1] 2 pole - 3 000 rpm.
    2] 4 pole - 1 500 rpm.
    3] 6 pole - 1 000 rpm.
    4] 8 pole - 750 rpm.

  5. #5
    Senior Member Rossluck's Avatar
    Join Date
    Dec 2005
    Location
    Gold Coast
    Age
    65
    Posts
    105

    Default

    Thanks for the advice Bob and elkangorito. I just looked up the RPM's of Honda motors and they run at maximum power at 3,600. This means that according to the table produced by elkangorito the motor should run at 3000 RPM without much trouble. I was testing it in the shed and maybe that's why I thought it was screaming. I might test it with a tacho and see what it's actually doing.

    But I also would like to hear more about brush motors. If it won't harm them to run at less than 50Hz, maybe I could drop it down a bit when drilling and so on.

  6. #6
    A Member of the Holy Trinity echnidna's Avatar
    Join Date
    Feb 2003
    Location
    Timboon VIC AUSTRALIA
    Posts
    2,746

    Default

    Quote Originally Posted by elkangorito View Post
    Just curious Bob, what's the difference you are talking about?


    To produce 50Hz, the following applies;

    1] 2 pole - 3 000 rpm.
    2] 4 pole - 1 500 rpm.
    3] 6 pole - 1 000 rpm.
    4] 8 pole - 750 rpm.
    The tables accurate,
    but Rossluck wanted 50cps at a lower engine speed so he needs to gear it up so the alternator will run at the correct speed while the engine runs at his preferred speed.
    Regards
    Bob Thomas

    ==================================
    Ebooks For Sale

    Doll House Book Shelf PLANS

  7. #7
    Timber Hoarder Cliff Rogers's Avatar
    Join Date
    Sep 2002
    Location
    Minbun, FNQ, Australia
    Age
    65
    Posts
    1,950

    Default

    Quote Originally Posted by Rossluck View Post
    ....This means that according to the table produced by elkangorito the motor should run at 3000 RPM without much trouble. .....
    That is for direct drive, if you have pulleys that are different sizes, you will need to factor in the gearing ratio which is what Bob is getting at.

    If you can get a shaft drive tacho to measure the speed it will help heaps.

    I know that the cheap direct drive gen sets run at high revs & eat fuel.
    The ones designed to run at slower revs & use less fuel cost more because of the engineering in them.
    Cliff

    ...if all you have is a hammer, everything looks like a nail...

  8. #8
    Registered User
    Join Date
    Sep 2007
    Location
    Nowhere
    Posts
    638

    Default

    Please bear in mind that the speeds I quoted are the speeds at which the "alternator" is supposed to operate to achieve the desired Hz. This may not relate to the rpm of the motor, particularly if gearing is involved as Cliff Rogers said.

  9. #9
    Registered User
    Join Date
    Sep 2007
    Location
    Nowhere
    Posts
    638

    Default

    Quote Originally Posted by Rossluck View Post
    But I also would like to hear more about brush motors. If it won't harm them to run at less than 50Hz, maybe I could drop it down a bit when drilling and so on.
    Ross, this has nothing to do with brush vs brushless motors. Your main concern is the equipment you wish to supply with electricity. If you can't produce a 50Hz supply, you are at risk of damaging equipment.

  10. #10
    Senior Member Rossluck's Avatar
    Join Date
    Dec 2005
    Location
    Gold Coast
    Age
    65
    Posts
    105

    Default

    Quote Originally Posted by elkangorito View Post
    Ross, this has nothing to do with brush vs brushless motors. Your main concern is the equipment you wish to supply with electricity. If you can't produce a 50Hz supply, you are at risk of damaging equipment.

    Fair enough elkangorito. I can't argue.

    I changed the pully this afternoon. First I went the wrong way and put a smaller pully on the motor, but when I struggled to reach 50 Hz again I had to sit down and dredge up memories of my push-bike years and the gear ratios. Common sense prevailed and I had a larger pully at hand that I installed.

    I think it's about right now. I've been testing it on a one HP bench grinder that sucks a lot of power at startup, and the motor gives a grunt when I flick the switch but handles it without too much trouble. Just guessing, I think I'm running at 50 Hz at about 2000 to 2500 revs. But either way the motor handles it at a moderate and reasonable number of revs.

    One more question: what sort of tolerance is allowable, is it say between 48 and 52 Hz?

  11. #11
    wood welder
    Join Date
    Dec 2006
    Location
    Canberra
    Age
    43
    Posts
    133

    Default

    Quote Originally Posted by elkangorito View Post
    Please bear in mind that the speeds I quoted are the speeds at which the "alternator" is supposed to operate to achieve the desired Hz. This may not relate to the rpm of the motor, particularly if gearing is involved as Cliff Rogers said.
    Thats what he said he is trying to do. Keep the alternator speed up with lower engine revs.

    Just because its a honda copy doesn't mean it will run the same. If you ever lift the heads off a cheap copy the ports will definitely look different, with rough burrs and casting marks. Having said that roughened ports can increase torque at lower revs by creating turbulence and increasing the swirling effect in the combustion chamber and can make the engine more efficient at a lower speed.

    Not to be taken as gospel of course but is certainly possible.

  12. #12
    Senior Member Rossluck's Avatar
    Join Date
    Dec 2005
    Location
    Gold Coast
    Age
    65
    Posts
    105

    Default

    Quote Originally Posted by Timmo View Post
    Thats what he said he is trying to do. Keep the alternator speed up with lower engine revs.

    Just because its a honda copy doesn't mean it will run the same. If you ever lift the heads off a cheap copy the ports will definitely look different, with rough burrs and casting marks. Having said that roughened ports can increase torque at lower revs by creating turbulence and increasing the swirling effect in the combustion chamber and can make the engine more efficient at a lower speed.

    Not to be taken as gospel of course but is certainly possible.

    Thanks Timmo. I don't actually trust Chondas, but the motor that I'm using has been very reliable on a compressor that I was using on building sites. The only problem I had with it was that the muffler kept coming off, and no matter how hard I tried I couldn't fix it. On the generator I was able to solve this problem by using a long muffler from another motor that I bolted to the frame holding the generator. On top of that, the generator and motor are bouncing on rubber, so that should reduce vibration.

  13. #13
    Senior Member Rossluck's Avatar
    Join Date
    Dec 2005
    Location
    Gold Coast
    Age
    65
    Posts
    105

    Default

    Quote Originally Posted by Cliff Rogers View Post
    That is for direct drive, if you have pulleys that are different sizes, you will need to factor in the gearing ratio which is what Bob is getting at.

    If you can get a shaft drive tacho to measure the speed it will help heaps.

    I know that the cheap direct drive gen sets run at high revs & eat fuel.
    The ones designed to run at slower revs & use less fuel cost more because of the engineering in them.
    Thanks Cliff. I borrowed my brother's tacho and had it for about two years. Just recently I gave it back to him, and I've never needed it more .

  14. #14
    Timber Hoarder Cliff Rogers's Avatar
    Join Date
    Sep 2002
    Location
    Minbun, FNQ, Australia
    Age
    65
    Posts
    1,950

    Default

    Quote Originally Posted by Rossluck View Post
    Thanks Cliff. I borrowed my brother's tacho and had it for about two years. Just recently I gave it back to him, and I've never needed it more .
    That is like having a clean out... as soon as you chuck it out, you will find a use for it.
    Cliff

    ...if all you have is a hammer, everything looks like a nail...

  15. #15
    Registered User
    Join Date
    Sep 2007
    Location
    Nowhere
    Posts
    638

    Default

    Quote Originally Posted by Rossluck View Post
    One more question: what sort of tolerance is allowable, is it say between 48 and 52 Hz?
    Frequency tolerance is up to the equipment receiving the frequency. Usually, wire wound equipment like electric motors, heaters etc, are quite tolerant to a slight increase in supply frequency than they are to a decrease in supply frequency. Electronic equipment may not be so tolerant.

  16. #16
    1K Club Member
    Join Date
    Oct 2007
    Location
    Adelaide
    Posts
    1,664

    Default

    Quote Originally Posted by Rossluck View Post
    One more question: what sort of tolerance is allowable, is it say between 48 and 52 Hz?
    Depends on what you're running from it. A light bulb won't care at all (though you'll see visible flicker if you run too slow) whereas it's an important issue for motors etc.

    The standard for the grid under "normal" conditions is 49.85 to 50.15. It will vary if something goes wrong such as a power station breakdown, failure of a major transmission line etc. Worst case when lots of things go wrong it's supposed to remain between 47 and 52 Hz - outside those tolerances things (eg suburbs, cities, large factories) get switched off to avoid equipment damage and assist in stabilising the grid.

    If it gets much outside that range then all sorts of nasty things happen and we all end up in the dark. That can happen rather quickly (minutes, seconds) if enough goes wrong all at once.

    I'd be trying to keep your generator between 47 - 52 Hz unless you're not running anything sensitive to frequency. As I said, light bulbs don't mind even 100 Hz but you'll cook the bearings in your tools pretty fast running them at that rate. Too low and you'll overheat motors etc and burn them out.

  17. #17
    Senior Member Rossluck's Avatar
    Join Date
    Dec 2005
    Location
    Gold Coast
    Age
    65
    Posts
    105

    Default

    Thanks Smurf.

Similar Threads

  1. Replies: 16
    Last Post: 19th Apr 2008, 05:11 PM
  2. Air-con question
    By Mark CH in forum Heating & Cooling
    Replies: 2
    Last Post: 29th Nov 2007, 12:39 PM
  3. A question Rod?
    By Jacksin in forum Plastering
    Replies: 1
    Last Post: 25th Oct 2007, 04:43 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •