    Hi all,
    Im about to build my second deck and wanted to know how deep you dig your holes for posts or stirrups.
    On my first deck I dug my holes 600mm deep with a diamater of 300mm as this was the advise I was given, but I intend to use stirrups on my next deck and cant find any that will go more than 400mm into the ground. would I still go for 600mm deep or is this overkill?

  2. #2
    Senior Member brynk's Avatar
    Join Date
    Sep 2007
    Location
    Canberra
    Posts
    156

    Default

    gday - it depends on a number of factors... so bear with me!

    without knowing specifics of your design, some things for you to consider...
    - stirrups (a u-shaped piece of flat steel - i think they're called cyclone stirrups) as opposed to the posts (with a steel tube 'welded' to the post's sole-plate) will be stronger
    - if you cast your stirrups into the ground, aim to get a minimum of 50mm covering concrete around the steel; likewise if you dynabolt or ramset your stirrups to the top of your footing
    - the more posts you have the smaller your footings can be because the more the downward forces are spread over footings, however
    - the more lateral forces you have acting on the tops of your posts, the deeper your footings will need to be (or you need to brace your posts)
    - if you decide to go deep then you don't necessarily need to have your stirrups going to the base of your footings; you could use reinforcement bent into the u-shape like the stirrup then wire the ends of the re-bar to the sides of the stirrup, once this is cast into the concrete it will be almost as strong because the concrete will lock it in eddy.

    our deck (currently in the timber procurement phase) is 30sq.m - 3m x 10m long - the 3m joists come out from the house & are picked up by a bearer resting on 4 posts, roughly 500 above the ground. the base of the footings are down 600, with a 200 deep bed of concrete placed in the bottom. each 100x100 hardwood post is then placed onto the cured concrete pad & backfilled. there is no roof but the posts will support a beer-rail.


    if our posts were 1600 above the footings then they must be dug in 800 deep, but the concrete would not change.

    the main goal of the stirrup is to tie the post to the footing (as well as provide clearance between the bottom of the post & the ground) - think of the posts as cantilevers and the depth of the footing as the back-span (hold a pencil in your fist to help you envisage).

    so on a deck the lateral forces applied to the tops of the posts are generally less than the downward ones, but do exist; they increase the higher your posts are, or if the deck has an open area underneath that has at least one wall exposed to the wind, or if your deck has a roof. the longer your posts are the more these forces are amplified (short pencil vs long pencil).

  3. #3
    Apprentice (new member)
    Join Date
    Sep 2007
    Location
    Melbourne
    Posts
    11

    Default

    Hi brynk,

    I'm planing a deck of 6.6mx3.2m, it has a very low clearance of 150mm to 250mm, so there is not enough space for bearers. I'm thinking to go straight to mount joists to stirrups and then put decking boards straight onto these joists. Is it all right to do so?

    I've been searching this great forum for advice and ideas but haven't found much about setting up the footings in this way.

    If I setup the joists from my house out, how do I make sure they're level? What I learnt from this forum is I can cut the tops off if they're wooden posts, so I don't have to worry too much when I plant the posts. Shall I better go this way, use wooden posts instead of stirrups? Then use joist hangers to mount joists to posts?

    Even with the later idea, what sort of saw I'd better use to make sure I cut the post tops off at water level when they're already in the ground?

    Many thanks,

    Ray

  4. #4
    Member
    Join Date
    Dec 2005
    Location
    geelong
    Posts
    75

    Default

    gday. You could put stumps in ground and use 140 x 45mm as bearers bolted tot he sides of stumps and use the same size timber as joists mounted 'internally' of the bearers usinh joist hangers.This way all bearers and joists are the same hight and with decking will have total hight of 160mm. Not ideal clearance but will work. i prosume it will be 3.2 out from the house. you will need three rows of posts if using 140 x 45 or a ledger fixed to house and two more rows of posts. To get them level use a straight edge (something straight and long) and sit one end at house where you want the deck to finish and have the other end over the last (or middle) stump hole. use spirit level on straight edge to make sure it is level and measure fron straight edge to bottom of hole (or top of sole plate). Remember to subtract the hight of the decking ie.20mm and cut stumps to this lengh. Put the whole frame up and check level then rapid set concrete the stumps in last. Then all you need is to put the decking on.

  5. #5
    Senior Member
    Join Date
    Apr 2006
    Location
    Melbourne Victoria
    Posts
    351

    Default

    Dan, 600 mm is a farily common depth. Depends on the overall size of the deck. The diameter of the hole depends on the area each post is supporting. THe depth is mainly to put the pressure down on compact soil. There would be no need to go any deeper. If you are using stirrups the depth of the hole provides little resistance against lateral forces, as the joint between the stirrup and post acts like a hinge.

    My last deck had 3 500w x 500deep post holes to support 3 steel posts. (engineer specs) These were 2.5 metres high under the deck and held a span of 6 metres. 40sqm deck off the side of the house.

    Ray for your question just using joists is not a good idea. some of eth posts may settle and the corresponding joist will sink, while the others stay at the same level. If a post settels under a bearer than that movement is spread over the bearer and all the joists connected, making it less noticeable.

    Joists don't have to sit on bearers, but can be attached to the side with joist hangers. That way the tops of the bearer and joists are the same

  6. #6
    Apprentice (new member)
    Join Date
    Sep 2007
    Location
    Melbourne
    Posts
    11

    Default

    Yes, it is 3.2m out from the house, now I know the secret to setup the stumps!! I’ll use 3 rows, 5 stumps in each row, so the total of 15 stumps, each of them are 1500mm apart.

    But mako, I might don’t understand what you’re saying of ‘mount joists internally’ – do you mean I need to cut the joists to 1500mm long each to fit them inside between every two rows of bearers?

    <OI will use 90x19 Merbau as decking board, is it ok to set joists every 500mm? In this way, I’ll need probably 13 lines of joists, say 26 pieces of joists all together?
    <O</O
    <O</O
    By the way, what sort of tools would be ideal to dig these 15 stump holes? I found a manual ‘cyclone hole digger’ in Bunnings, it costs about $55, would it be ok? Do I have to dig 600mm deep for the 5 holes close to the wall, where the stumps will be only 150mm above the ground?

    Cheers,
    Ray

  7. #7
    Apprentice (new member)
    Join Date
    Sep 2007
    Location
    Melbourne
    Posts
    11

    Default

    I found the answer from another thread, yes, I have to cut the joists

    Please still answer the rest of my questions about the hole digging tool.

    Thanks,
    Ray

  8. #8
    Member
    Join Date
    Dec 2005
    Location
    geelong
    Posts
    75

    Default

    if using the 140 x 45 you just nail joist hangers along the bearer and fix in the 140 x 45 joists into the so basically the top of your joists are level with your bearers. So from your house you will have a row of posts spaced at 1500mm with a bearer of 140 x 45 bolted to it. Then you will have another bearer out 1600mm from the 1st one. Then your last (outer) bearer another 1600mm out. this will give you the 3.2m from house. then mark long each bearer 450mm and nail a joist hanger at each mark. Then cut 140 x 45 joist to fit between each bearer, taking into acount the thickness of the bearers to get you 3.2m off house. and also make sure you can get the 1st bearer right up against the house or you will have a gap between your deck and house. If you cant you will have to mount the 1st beaeer to the house directly. The reason i said you can span your joist 1600mm is if you are using the 140 x 45mm method. This size timber can span 2.6m when used for joists. the 1500mm max span quoted earlier was for using 90 x 90 (or 2 90x45's) bearers and 90 x 45 joists. This meathod would siut also if you cant get your 1st row of stumps right up to the house because you can overhang the joist (because they sit on top of bearers) up to 300mm. As for digging the holes it depends on the ground. if it is hard clay you can either put the hard yards in by hand or hire a post hole digger. If you do get the canterlevered on so you dont go for a ride if it grabs. They are about $80 per day i think from kennards or less for 4 hours. If it is rocky a crowbar and shovel is best. As for the depth with a deck this hight (not very high) you would only need to go down about 300-400mm into CLAY. If you have 200mm of fill on top of natural clay you will need to dig 500-600 from surface. use a sole plate and concrete. Also you could span 500mm with 90mm merbau but i would keep it at 450 to reduce bounce. It will make a differance.

  9. #9
    Apprentice (new member) Rough Sawn's Avatar
    Join Date
    Jul 2007
    Location
    Sydney
    Posts
    5

    Default

    Quote Originally Posted by remonyan View Post
    I found the answer from another thread, yes, I have to cut the joists

    Please still answer the rest of my questions about the hole digging tool.

    Thanks,
    Ray
    If by cyclone post hole digger you mean one like this:



    TRUST me, your MUCH better of with one of these 'scissor shovels':



    Also a pinch bar would help should you encounter rock or hard clay.

    Or you can take the easiest approach and do as mako suggested and hire a petrol powered post hole digger.

  10. #10
    Senior Member
    Join Date
    May 2007
    Location
    Williamstown, Victoria
    Posts
    106

    Default

    Hire shops only charge around $70 for half day use of a petrol powered post hole digger. Should be able to dig a hole within 5 to 10 mintues or so, not a bad option.

  11. #11
    Senior Member
    Join Date
    Oct 2006
    Location
    ACT
    Posts
    347

    Default

    I used a petrol powered 2 person hole driller for my last deck and i can tell you its not for the faint hearted. After 25 holes our bodies were aching. You need to be very carefull with them, dont get the missus to help as she wont be able to handle it, especially if its clay and/or rocky.
    Im using the conventional shovel, crowbar, pick and wheelbarrow this time.
    But as williamstown said its only 5-10 minutes a hole.

  12. #12
    Member
    Join Date
    Dec 2005
    Location
    geelong
    Posts
    75

    Default

    if doing it yourself hire the canterlevered petrol powered post hole digger. It has a set of wheels and the augerat one end with handles and the motor at the other end. if it jams it will just stop the auger and not spin the operator. Ive used them hundreds of times without any problems. The only problem is they can be a little gutless in hard ground. If it is a large deck with lots of holes and you need to go deep hire a dimgo for half a day. Great fun to use too.

  13. #13
    Apprentice (new member)
    Join Date
    Sep 2007
    Location
    Melbourne
    Posts
    11

    Default

    I might have to leave a 20mm gap between the brick wall and the first bearer, the reason being if I bolt the first bearer to the wall, due to the limit height clearance I have on this end – only 150mm, it will block several air flow windows the builder built in the wall, these small windows are below the floor level, I guess this is designated to let air flow through underneath the floor? In this situation, is 20mm gap big enough? I hope so.<?xml:namespace prefix = o ns = "urn:schemas-microsoft-comfficeffice" /><o></o>
    <o></o>
    The post hole digger I looked at Bunnings was the red color ‘scissor shovels’ that Rough Sawn attached here. I also saw the green color real ‘cyclone’ but I didn’t like it. Thanks for clarify it, Rough Sawn. Mako’s ‘canterlevered petrol powered post hole digger

    ’ sounds interesting, I’ll go to hire shop this Saturday to have a look at it, my concern is like what happened to Dan, it’s probably a bit hard to handle by a newbie like me

  14. #14
    Senior Member
    Join Date
    Oct 2006
    Location
    ACT
    Posts
    347

    Default

    Ok Guys, I have dug 15 of my 40 or so holes and have hit water at about 900mm on two of them!! I am on a canal so ground is about 2-3 metres above the tide mark, We had a bit of rain a few weeks ago so Im thinking the water has built up from this. the holes are close to my retaining wall (pics in this link http://www.woodworkforums.ubeaut.com...ad.php?t=56662 )
    is this going to cause me any issues? (its all clay if that matters)

  15. #15
    Member
    Join Date
    Dec 2005
    Location
    geelong
    Posts
    75

    Default

    remonyan, 20mm clearance for air flow should be fine. But you dont want a 20mm gap between your house and 1st deck board. if you are puttin joists on top of bearers run the joists right to the house. If joists not on top you may have to overhang your 1st deck board over bearer but no more than about 10-15mm. Thsi would leave a gap of around 5mm between deck and house... not ideal visually but should look ok. Also dont worry about using the post hole digger i suggested. very easy and safe. They look a bit intimidating but trust me they are a peice of p***.

  16. #16
    Member
    Join Date
    Dec 2005
    Location
    geelong
    Posts
    75

    Default

    dan. Why did you go so deep, especially if it is all clay. Holes for stumps for a deck low to the ground, using sole plate and concreted in only have to be min. 300mm x 300mm into CLAY. This is minimum and i would go about 450mm into clay but not 900mm ! Too much work anyway. lol

  17. #17
    Senior Member
    Join Date
    Oct 2006
    Location
    ACT
    Posts
    347

    Default

    I have only gone 450mm deep on most holes except for the the two I have hit water. I kept digging because the ground got too soft so I tried to get harder ground, which ended up being water.
    If i put a sole plate in will it be ok to fill with concrete without the worry of the post sinking?

  18. #18
    Apprentice (new member)
    Join Date
    Sep 2007
    Location
    Melbourne
    Posts
    11

    Default

    Dan, I could be wrong though but why don't you refill some dirt or small stones back to those two BIG holes, then use sole plates in them?

    Ray

  19. #19
    Senior Member
    Join Date
    Oct 2006
    Location
    ACT
    Posts
    347

    Default

    I think thats what I will do, I might put a little dry concrete in below the sole platel aswell.

  20. #20
    Member
    Join Date
    Dec 2005
    Location
    geelong
    Posts
    75

    Default

    Probably best to put in some crushed rock. then about 100 -200mm of concrete, let it set, us ethis as your sole plate and put stump in and more concrete. wont go anywhere then.

  21. #21
    Apprentice (new member)
    Join Date
    Sep 2007
    Location
    Melbourne
    Posts
    11

    Default

    I’ll go for 145x45 bearer and joist as mako recommended, this is my only option because I have a small concrete slab (1780x1000) just outside the backyard sliding door, so I can’t dig down to gain clearance The 1500mm clearance on the house end is the measurement from the surface of this concrete slab to the surface of the floor in the house. So I have two issues:
    <?xml:namespace prefix = o ns = "urn:schemas-microsoft-comfficeffice" /><o></o>
    1 The deck surface will be 145+19-150=14mm above the floor in the house, my concern is when it rains, the water will flood into the house from under the sliding door. How do I stop this from happening? Seal the bottom of the door from inside and outside?
    2 I have to skip one stump in the concrete area due to its length of 1780mm > 1500. I’ll leave the first bearer straight onto the concrete, so I’ll have to use H4 timber for my first bearer. Is it ok to go this way? Remove that piece of concrete sounds too hard, don’t know how deep it goes into the ground. Any better idea?

  22. #22
    Member
    Join Date
    Dec 2005
    Location
    geelong
    Posts
    75

    Default

    ok. I think i understand what you are saying. To span over your slab you could use 120 x 45 which can span 2200mm You could actually use this size for all your joists but still use 140 x 45 bearers. 120 x 45 can be hard to find at some timber supliers (eg Bunnies) or you could cut some down to size from 140. How are you going to attach the 1st bearer near the house? Can you mount it to the house under the door sill? if not you will have to anchor it down th concrete with brackets but it will have to be about 126mm (x 45mm)...126mm bearer, 19mm decking and 5mm under door hight = 150mm. Once youve attached this bearer span the 120mm joists over the concrete and have the next bearer just past the slab which you can attach to stumps.

  23. #23
    Apprentice (new member)
    Join Date
    Sep 2007
    Location
    Melbourne
    Posts
    11

    Default

    Mato, I’ve attached a rough drawing to help understanding my situation, if I can’t use 120x45 as bearer and I can’t bolt the 1<SUP>st</SUP> bearer to the wall because it will block those air holes. Then my plan is as in the drawing: I’ll plant 4 stumps in the 1<SUP>st</SUP> row for the 1<SUP>st</SUP> bearer (140x45), bearer will bolt to stumps and the green part of the bearer will sit directly to the slab. Red color is the small gap (<20mm) I’ll leave to air flow. Stump 1 will span 3000mm to Stump2 (green part of bearer in slab), Stump2 will span normal size (1500) to Stump3. In this plan, joists will be 140x45 or 120x45.
    Attached Thumbnails Attached Thumbnails decking2.jpg  

  24. #24
    Member
    Join Date
    Dec 2005
    Location
    geelong
    Posts
    75

    Default

    Ok, now i understand. Sounds ok to do it the way you say but am i right that you have only 150mm from slab to door level? if this is the case you will have to 'check' out 10mm from the bottom of the bearer where it goes over the slab so the total decl level is same a door.

  25. #25
    Apprentice (new member)
    Join Date
    Sep 2007
    Location
    Melbourne
    Posts
    11

    Default

    Yes, I only have 150mm from slab to door level - that's the pain

    If it's ok to 'check' the bearer off 10mm, it'll flush the door level! If I do this, the bearer will still sit on the slab, do I need staining the bottom of the bearer?

    Ray

  26. #26
    Member
    Join Date
    Dec 2005
    Location
    geelong
    Posts
    75

    Default

    Yeah i would seal the timber where it will sit on the slab, even with some paint and if your fussy lay a strip of malamine under it. You can get this stuff from hardware stores and looks like tar. Just works as a moisture barrier. You might even look at putting an angle bracket in the middle of the slab to hold the bearer in place.Just some sort of galvanised strong bracket and dyna bolt to slab and screw to timber. Not essential but wont hurt.

  27. #27
    Apprentice (new member)
    Join Date
    Sep 2007
    Location
    Melbourne
    Posts
    11

    Default

    Thanks, mato. I almost come to the last bit of this plan - when I bolt the bearers to stumps:

    1. what sort of bolt would you recommend?
    2. I guess two holes per stump (90x90 t pine stump, 120x45 bearer and joist) would be enough, but at what position should I drill these two holes? I attached a drawing for this, but not sure if there's any rule of how far the hole should be kept from the side and top of the stump? How far the holes should be kept apart?
    3. Any other tips for bolting?

    Thanks heaps,
    Ray
    Attached Thumbnails Attached Thumbnails holes.jpg  

  28. #28
    Senior Member Burnsy's Avatar
    Join Date
    Apr 2007
    Location
    Kalamunda
    Age
    51
    Posts
    191

    Default

    Quote Originally Posted by remonyan View Post
    Thanks, mato. I almost come to the last bit of this plan - when I bolt the bearers to stumps:

    1. what sort of bolt would you recommend?
    2. I guess two holes per stump (90x90 t pine stump, 120x45 bearer and joist) would be enough, but at what position should I drill these two holes? I attached a drawing for this, but not sure if there's any rule of how far the hole should be kept from the side and top of the stump? How far the holes should be kept apart?
    3. Any other tips for bolting?

    Thanks heaps,
    Ray
    Go the first option with M10 (10mm) galv cup head bolts and galv washers under the nuts.

  29. #29
    Member
    Join Date
    Dec 2005
    Location
    geelong
    Posts
    75

    Default

    Yeah fig. 1 is the go. You could also 'house' out the top of the stump where the beaeer will attach, so effectively the bearer has a lip to sit on. You dont have to house it out full 45mm, maybe 25mm.

Similar Threads

  1. Bolt-on Post Support v Full Stirrup.
    By Dr - 307 in forum Pergolas, Gazebos, Strombellas & Rotundas
    Replies: 20
    Last Post: 27th Feb 2008, 07:42 AM
  2. Veranda post and deck bearer sharing a stirrup?
    By Williamstown in forum Decking
    Replies: 6
    Last Post: 26th Sep 2007, 09:36 AM
  3. Replies: 3
    Last Post: 24th Apr 2007, 09:35 PM
  4. Post Anchor/Stirrup question
    By reilly in forum Decking
    Replies: 5
    Last Post: 9th Feb 2005, 05:32 PM
  5. Filling big holes to make smaller holes
    By Sir Stinkalot in forum General Odds & Sods
    Replies: 9
    Last Post: 4th Oct 2003, 12:51 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •