Solar wire gauge question

Results 1 to 11 of 11
  1. #1
    Novice
    Join Date
    Nov 2014
    Location
    Sydney
    Posts
    41

    Default Solar wire gauge question

    I'm wiring up my batteries and the MPPT charge controller. I've used 160amp wire for the 12V battery system in parallel, through to the 240V inverter. My question is does the wire gauge from the charge controller into the batteries have to be the same gauge (ie 160amp)?

    The solar people I bought the system from said I only need to use the 4mm2 wire that came with the panels (2 x 200W), but I'm not so sure. The 160amp wire is too large to fit into the charge controller terminals.
    The inverter is 2800w, but don't intend to use it's full capacity. Might draw 1500W at the most.

    4mm2 or 160amp?

    Thanks.

  2. #2
    1K Club Member Random Username's Avatar
    Join Date
    Jul 2012
    Location
    Canberra
    Posts
    1,185

    Default

    Might need a few more specs.... a cable capable of carrying 12 volts/160 amps DC will be somewhere in the region of 35-40mm diameter. The ah refers to the charge holding capacity of the battery. What's the maximum charging current that the (whatever) can deliver to charge the batteries?

    But a good guide is the controller terminals - if the cable is too big to fit, it's oversized for the rated output (assuming decent engineering and not chinese 'we have 10,000 of these on the shelf that were rejected by the firm whose design we are ripping off' engineering).
    DIY electrical house wiring details suitable for Australia - http://goo.gl/9d33T (PDF file)

  3. #3
    Novice
    Join Date
    Nov 2014
    Location
    Sydney
    Posts
    41

    Default

    Sorry meant to type amps (a) not ah....duh. Will edit now.
    The terminals on the charge controller will only take 10mm diameter cable. The cable I have for the batteries and inverter is more like 14mm.
    The controller is a 30A unit.

    Thanks mate.

  4. #4
    1K Club Member Random Username's Avatar
    Join Date
    Jul 2012
    Location
    Canberra
    Posts
    1,185

    Default

    Minimum 6mm assuming your run is only short (10 meters or so). If you have a longer run, you might want to take voltage drop into account and upgrade to 10mm.
    DIY electrical house wiring details suitable for Australia - http://goo.gl/9d33T (PDF file)

  5. #5
    1K Club Member UseByDate's Avatar
    Join Date
    Sep 2014
    Location
    South Australia
    Posts
    1,259

    Default

    Quote Originally Posted by Random Username View Post
    Might need a few more specs.... a cable capable of carrying 12 volts/160 amps DC will be somewhere in the region of 35-40mm diameter.

    .
    Are you sure this is correct? 40 mm diameter cable to carry 160 amp seems excessive to me.
    “What a fool believes, he sees. No wise man has the power to reason away”- The Doobie Brothers

  6. #6
    1K Club Member
    Join Date
    Feb 2007
    Location
    Sydney
    Posts
    1,272

    Default

    One would assume he means 40mm2 cable, which has a much smaller diameter, but it can be very misleading to those who don't understand cable sizes!

  7. #7
    4K Club Member Marc's Avatar
    Join Date
    Jul 2003
    Location
    Sydney
    Posts
    13,215

    Default

    I would install 50 mm diameter just to be on the safe side ...

    A quick calculation tells me that a 50mm diameter is over 1900 mm2 and a 40mm2 is a tad over 7mm diameter. Talk about misleading !

    surface of a circle is the square of the radius (diameter /2) times 3.14
    Whenever you find yourself on the side of the majority, it is time to pause and reflect
    Mark Twain

  8. #8
    1K Club Member UseByDate's Avatar
    Join Date
    Sep 2014
    Location
    South Australia
    Posts
    1,259

    Default

    Plus a “tad” more for the air between the wire strands in the cable.
    I assume you are using the metric “tad” in this context. I prefer to use the imperial “tad” when dealing with SWG (Standard Wire Gauge).
    “What a fool believes, he sees. No wise man has the power to reason away”- The Doobie Brothers

  9. #9
    1K Club Member
    Join Date
    Feb 2007
    Location
    Sydney
    Posts
    1,272

    Default

    Not that I've ever seen it, but if it were a single strand... then Marc is spot-on

  10. #10
    4K Club Member Marc's Avatar
    Join Date
    Jul 2003
    Location
    Sydney
    Posts
    13,215

    Default

    Now now you two ... you are straining the gnat, are you telling me you have never seen a 1900mm2 single strand wire?

    I remember working in a shut down where a guy got busted for smuggling a foot of (304.8 mm give or take a metric tad) a very thick single strand cable stored in the warehouse. It was easy 50mm in diameter and in a massive roll. This guy would go everyday with a hacksaw and cut a bit off and put it in his lunch box. Eventually he got busted.
    Whenever you find yourself on the side of the majority, it is time to pause and reflect
    Mark Twain

  11. #11
    Senior Member
    Join Date
    Jun 2010
    Location
    brisbane
    Posts
    373

    Default

    Quote Originally Posted by Window575 View Post
    I'm wiring up my batteries and the MPPT charge controller. I've used 160amp wire for the 12V battery system in parallel, through to the 240V inverter. My question is does the wire gauge from the charge controller into the batteries have to be the same gauge (ie 160amp)?

    The solar people I bought the system from said I only need to use the 4mm2 wire that came with the panels (2 x 200W), but I'm not so sure. The 160amp wire is too large to fit into the charge controller terminals.
    The inverter is 2800w, but don't intend to use it's full capacity. Might draw 1500W at the most.
    Hi I
    If you are referring to the battery charging lines from the MPPT controller ??, the size will depend on the solar panels total rating, the battery bank voltage & the actual distance the cables have to run[A to B]
    The size you use for your inverter has nothing to do with the solar[Unless you are using a MPPT that monitors load }
    And for 160A Short distance 1 B&S/AWG[42 sqmm cross sectional AREA[NOT DIA],which is around 7.5MM. actual copper dia] or 50mm metric cable has a continuous current rating of 165A

Similar Threads

  1. Warranty Question re Solar Hot Water Tank
    By vgreen in forum Solar Electrical Systems
    Replies: 3
    Last Post: 29th Jun 2012, 06:30 PM
  2. iPhone as a Bevel Gauge
    By Blocklayer in forum Announcements
    Replies: 3
    Last Post: 23rd Sep 2010, 09:11 PM
  3. Galvinised wire gauge for fencing?
    By Mcblurter in forum Landscaping, Gardening & Outdoors
    Replies: 3
    Last Post: 1st Feb 2009, 10:36 PM
  4. Replies: 8
    Last Post: 1st Oct 2008, 10:43 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •